MG Thermal Consulting Posted March 29, 2019 Share Posted March 29, 2019 Just did a large distillery mash cooling selection- Using a 60 Ton chiller with a two fan EMSCO glycooler vs a 100 Ton chiller is about $10,000 more on equipment but saves 37 Kw per hour energy during operation, less than one year payback. This installation will be in the sweltering SE USA, but if I used it in the N. USA, savings would be close to 50 Kw per hr or more. Using just a straight drycooler saves 15 Kw per hour on a 20T. system during all close to 35F operation in Utah where water is scarce. 214-0022-VIRGA_III_Vs_TAC_Comparison_Chart_WEB.pdf Link to comment Share on other sites More sharing options...