  1. If you are going to use the water for the next mash run, then the chiller would need to have non-ferrous water passages (including pump),

    Easiest way is to meter water form city water source and match that to the still condenser usage.  

    I would do this from a CWT (non-ferrous) pressurized so you don't have bacteria buildup.

  2. Even better, a hybrid cooler- works like a drycooler in winter and an evaporative- adiabatic in summer.

    The hybrid controls when the chiller needs to be run.  Really handy if you will be running still and mash cooling at once.

    Recent project uses a 40 T. hybrid cooler and 60 T. chiller for mash cooling instead of 120 HP chiller.  Saving 40 HP of cooling for each run.

    Additional feature is a still chiller that reuses city water for next mash run.

     

  3. On 8/1/2019 at 2:36 PM, Birster74 said:

    What is the recommended water tank size to cool 240 gallons mash tun?

    Thank you

    For just the mash cooling, near a 500 Gal. You should be near 65-70 tank temperature when done, so then let the chiller to continue running until the tank is around 55F, and then you're ready  for still action!  If you're cooling fermenters too, you want to upsize the reservoir so it finishes up a little cooler since you want decent temperature going to the fermenter jackets. I would tap off the return line back to the tank from the chiller so you have coldest water going to the fermenters and then return that back to the tank.

    I tend to use a hybrid cooler now (not a dry cooler, but similar) that gives you 85F glycol in summer and colder all other seasons. I use a chiller for the still and fermenters when I need to- this is my current high efficiency design.

    This design also allows smaller reservoir tanks and much less KW used for cooling during off season. I have a 40 ton hybrid cooler and 60 ton chiller used for a quick mash cool in a large distillery where they are mashing every day.  They would have had to use 100 ton chiller if they did this with a large reservoir. I am saving 20 HP for the cooling in the summer and probably more like 40 HP in the winter season.

    Cost savings is immediate as well.

    • Thanks 1
  4. The sizing of the reservoir depends on the mash cooling time plus the fermenter cooling as well, so if you had a 250 Gal mash load, a 500 Gal reservoir for that plus extraneous loads like fermenters.  Recovery time should get done before you are ready to make a still run, so get the reservoir back down to around 50-55F before use again.  

    If you are doing stripping runs, you'll have to upsize the chiller in some cases, especially if the tank starts to overheat- creeping above 70F before you're not close to the end of the strip run is not a good sign and you should adjust technique so you don't overheat the chiller.

    I am adding a 2-stage cooling technique for larger mash runs by adding a hybrid adiabatic glycol cooler which will give you performance of a cooling tower with a closed loop system, so I can run it along with the chiller to take the high heat out of the mash run which reduces the chiller size and overall KW.  On a recently completed system, the savings winds up being 20 HP per hour of usage compared to cooling with a chiller.

    Hope to have pictures posted soon!

    • Thanks 1
  5. For such a small chiller, if you can set it under a roof vent to take hot discharge air off it outside, you should be able to use it indoors unless it would be really close to any ethanol vapor- thats a no-no.

    The chiller should not suffer too much with glycol at the same temperature output, you may need a little more flow on the glycol to offset the friction loss and inherent loss from glycol thermo properties.

  6. Hedge,

    More often than not, clients just fill the whole inside portion with water (treated) which simplifies it.

    The only reason glycol is added is to: 1) prevent winter free-ups, and 2) if you want to chill water below 45F, many manufacturers tell you to.

    Tapping off the glycol line allows you to lower the glycol temperature- handy for chill filtering- but you must valve the line off so the sub-freezing  glycol doesn't pass through the heat exchanger (if you have one) and freeze the water in the water loop of the heat -x.

    You certainly can have the chiller set lower, again depending on whose you have, but you should be able to get to 40F by adding glycol and re-setting thermostat.

    "Raw" water is often used in critical situations as a backup, only, situation like at hospitals, but it needs to have a rugged filter to keep silt out of the loop which will inevitably end up inside the chiller evaporator.  If you have a chiller that has a "coil inside a tank" design, this is not as critical because the water is outside of the tubing, settling in the tank.

     

  7. 7 minutes ago, HedgeBird said:

    The chiller we have is glycol, so I dont think this is an option for us, unless we change chillers.  Might need to start hunting for a brewers bright tank, as they typically have both jackets and insulation.  

    You need to add a small plate exchanger and second pump. Put globe valves on discharge of pumps so you can balance flow on HTX.  I have pix from one of clients, if you want to email me, I'll send them over.

  8. Thanks, Star!

    It's a tough thing to get through some clients that running a strip requires almost double capacity what a pot run will require- and just because you have oodles of tank capacity, doesn't mean successive strips and mash coolings will have you run out of tank capacity because the chiller was sized marginally or the boiler is over capacity and will try to do the strip in 3 hrs and your cooling was sized on 6 hrs.  

    Lately it seems to be common to have larger mash runs, more than twice the strip run volume and here is where a hybrid cooler can keep your chiller size down to the size of the run volumes and fermenters.

    Unequal size of batches will make tanks hot such that there isn't enough remaining to control a number of fermenter. 

    Like everything, best be wary of loads that are far apart in the calculations.

     

  9. I have supplied 5 HP chillers for 300 Gal pot stills, but more often than not, the customer is running a strip, so the load is much hotter an usually wind up supplying a 10 Ton instead, a couple fermenters are enough to make a 5 HP lacking. I really don't like chiller return water to get beyond 70F continuously, 75F continuously and you're asking for trouble on hot Summer days, overheating refrigerant compressors.

    I am supplying a chiller plus a hybrid air cooler on a large mash load (85 tons) down South right now and wound up selecting a 40 T hybrid cooler (runs like a cooling tower only dry circuited) on the first stage cooling and a 60 ton chiller on the 2nd stage rather than a 100 ton chiller.  Much more KW friendly and will allow a second mash run in the future.

    I have two types of dry or hybrid coolers, one very simple and the other like the hybrid variety which uses a water spray in the summer. Paybacks about 2 years or less. 

  10. You will need a very large reservoir to serve a 300 gal strip run with a 5 HP chiller.

    In addition, you will have a tough time keeping any fermenters and getting back to setpoint to chill mash.

    It is much better to go to an 10 ton chiller and 600 gal reservoir.

    Good luck and if you need a trouble free air glycol cooler to precool chilled return water, give me a shout. For the electric cost of a second pump and fan motor, it will save you kwh and have payback in less than a couple years, depending on your weather.

  11. 17 hours ago, Southernhighlander said:

    Bluebolt,  our stills have copper defuser plate assemblies that maximize your copper vapor interaction (among other things).  I came up with the design 7 years ago.  Just one of my defuser plate assemblies guarantees 100% copper vapor interaction.  Most of our stills have at least 2 defuser plate assemblies.  We have glass bubble plate columns and we have the 26 gallon pots as well as 40 gallon pot belly pots.  Our 40s cost less than our competitors 30 gallon pots.  

    I had to have an emergency surgery yesterday.  It will be 2 to 3 weeks before they will let me work in my office.  However, I have 5 office staff so everything will be running smoothly as always.  I have not been able to answer my emails since the surgery but I will be working from my bed on my lap top starting tomorrow.  

    If you would like to talk about your needs, give me a call at my home number tomorrow 417-778-6100.  Or if you would just like to order call 417-778-6100 and ask for Susan. Here is Susan's email address: susan@distillery-equipment.com  

    Get well soon, man! Healin' thoughts to ya!

     

    • Thumbs up 1
  12. I do offer small chillers for the chilling, but if you have a chiller now and have it charged with a glycol mix, pick an off day, lower the chiller thermostat to 25F and chill the spirit in a jacketed vessel, pumping the glycol through the jacket to lower the spirit temp to near 32F.  I have chillers that do this and even have a fancier one that does the switchover "push button" for a rum producer. I would touch base with your chiller provider for the OK.

    If you need any other info, give me a shout.

    Mike

×
×