  1. Fortunately, the short time the barrel is un-bunged was disregarded or they just don't care. Seems like they really want the distillery. Cant believe your getting that kind of response in Colorado
  2. Can you tell me where exactly you found "in-process" liquids are exempt from maq?
  3. Since IFC exempts wooden cask from potential hazardous containment classification, local building code shouldn't be able to restrict you capacity. An F-1 Classification due to flammable liquid storage would limit the volume per control room to 120 gallons NS or 240 with a sprinkler given your containment vessel is not exempt. Since it is, there is no fire barrier subdivision or capacity regulation, only a height restriction of 2 ft. from the ceiling. In other words disregard local code pertaining to maximum allowable amounts under F classification with or without sprinklers, IFC exemption supersedes.
  4. a small victory for Texas whisky men
×
×