Jump to content

tasting room distillary fire seperation


Recommended Posts

Hello friends,

Looking for info on fire seperation required between distillery: F1 (moderate hazard manufacturing) and tasting room: M (mercantile) tasting room is less than 10% of total square footge if that maters.

Greatly appreciate any help you can offer.

Link to comment
Share on other sites

Need to check with your local code AHJ, but if you're lucky enough to convince them your tasting room is M then there is no fire separation requirement with F1. Also note the 10% accessory occupancy would apply to just the M space, not your entire distillery. Tasting rooms are typically A. Fire separation between A and F1 is 1hr if sprinklered.

Link to comment
Share on other sites

  • 2 weeks later...

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...