We are looking to upgrade our spirit tanks and I can't tell if we need double walled tanks, exterior vents, etc.  I'm referencing NFPA 30 and UL-142.  We're talking about blending tanks and holding tanks in the 1000-1500 gallon range.  Is potable ethanol exempt from these?  Also, do you have recommendations for suppliers of these tanks if that is what I need? 

Cheers

Link to comment
Share on other sites

single wall tanks that are UL listed should meet your fire marshalls needs. For tanks that size either XP vacuum type exhaust or venting outside are both safe options to prevent the accumulation of flammable vapors

Link to comment
Share on other sites

This is what you need.  This is directly from NFPA 30.  Skolnik has what you need.  http://www.skolnik.com/

9.4.1* Only the following approved containers, intermediate bulk containers, and portable tanks shall be used for Class I, Class II, and Class IIIA liquids: (1) Metal containers, metal intermediate bulk containers, and metal portable tanks meeting the requirements of and containing products authorized by the U.S. Department of Transportation Hazardous Materials Regulations in Title 49, Code of Federal Regulations, Parts 100–199, or by Part 6 of the UN Recommendations on the Transport of Dangerous Goods

Link to comment
Share on other sites

My tanks are 250, 550 and 750 gallons and they are stackable.  They are rated for spirit storage and are stainless steel.  My pricing is much better than Skolniks per gallon and my tanks will store more ethanol in a much smaller space than the skolnik tanks.  

  • Thanks 1
Link to comment
Share on other sites

Must admit some of this seems less than clear, and so I welcome comments on what TTB (at their booth) at ADI in Portland told us --  that common plastic IBC totes were approved for bulk storage, which of course is not what Thatch has quoted from NFPA 30 above, or what Paul from Affordable (also above) has said.   They (TTB) also said that the MAQ was 240 gallons per zone (with up to 4 zones/facility - each sprinklered and vented), though I have heard lower volumes quoted also.   Does NFPA 9.4.1 refer to storage or transportation?   Thanks in advance,

Link to comment
Share on other sites

1 hour ago, et1883 said:

common plastic IBC totes were approved for bulk storage, which of course is not what Thatch has quoted from NFPA 30 above, or what Paul from Affordable (also above) has said.

Plastic totes are only approved for transport but you can walk into most any distillery and see them stacked floor to ceiling.  If a fire were to break out they melt and help to fuel the fire.  There may be specialized totes that will not melt but common plastic IBC totes are a problem.  You need to consult with the AHJ (fire marshall) to see what he will allow.

 

1 hour ago, et1883 said:

They (TTB) also said that the MAQ was 240 gallons per zone (with up to 4 zones/facility - each sprinklered and vented)

This is not under TTB's jurisdiction, it is part of the building codes.  The 240 gallon number is correct but can be doubled when you store in the containers that are listed in NFPA 30.  Dalkita is a respected expert in this matter.  The link takes you to a .pdf that attempts to make sense of the various specs that are in play.   http://www.americancraftspirits.org/wp-content/uploads/2016/05/Safety-Code-Breaking-Barrels.pdf.  If you wish to store in 55 gallon stainless, Skolnik's probably your best bet.  If you want larger, Paul will take care of you.

  • Thumbs up 1
Link to comment
Share on other sites

Thanks for the replies everybody! I appreciate the plugs but unfortunately I don't need 55 gallon drums - I need 1000-1500 gallon conicals for storing/blending/proofing spirits.  

I'd like to ask a few more questions from above & this weekend's thrilling investigation of codes... 

- I think the MAQ is 120 but can be doubled to 240 gallons when an automatic sprinkler system is present.  This is for non UL tanks right?  UL tanks far exceed 240 gallon and are commonly held inside a building too.

- a single wall tank is acceptable if you have a drainage containment tank for the facility and automatic fire suppression?  The quotes for double walled tanks are literally double and I don't want to spend 60k on tanks.. 

- are XP vacuum vents used in conjunction with atmospheric venting or separate?  Also, are these typically supplied by the tank mfc or purchased separately?

Cheers

Link to comment
Share on other sites

Hi Nabtastic,

For what it's worth, we recently moved locations (new fire and building approvals), and we had to modify 13 stainless steel single wall tanks with pressure release vents and sealed lid gaskets and lever rings, even while stored in our H3 (fire rated room), to comply with the spirit of NFPA. Plastic IBC totes are not usable for us at all upon landing at our facility, and we have full automatic fire suppression throughout the building. The 240 MAQ is in force for us anywhere outside the H3 storage room, which means 240 gallons of alcohol on the floor for us at any time, and its assumed that all tanks and distilling equipment are UL rated. Tank sizes did not matter in our situation. We had a issue with open vs. closed system in terms of distillation, but were able to keep the 240 MAQ with the open system, but they did initially want us to install a closed system (distillation directly to tank) vs. the open parrot into tank with open alcohol in the building, and threatened to drop our MAQ to 120 during that negotiation.

Oh, and we had to install an explosion proof fan in the H3 storage room with a direct vent to outside of the building (through the roof), and had to install and use near ceiling exhaust fans in the building when distilling/pumping/bottling, etc. And the ethanol detection system...

Good luck with the upgrades, sounds exciting!

  • Thanks 1
Link to comment
Share on other sites

Those who say this is not TTB's bailiwick are correct - sort of. 

When TTB says plastic totes are okay, it speaks only to what is within its jurisdiction, which in the case of the storage of distilled spirits, is established in the Internal Revenue Code.

Because jurisdiction springs only from the IRC, TTB's tank rules reflect revenue concerns.  I think that the rules -  as written as opposed to as enforced - go back to times when the DSP system was closed, i.e., to times of cap seals and government locks, when the proprietor was allowed no unsupervised access to spirits, until the spirits were first were gauged, in bulk, by a government employee, for tax determination.  Only then were they removed from government lock and key and turned over to the proprietor for rectification and bottling.   So, access to tanks had to be restricted.

Changes to the IRC, made in 1980, created the all in bond system under which you conduct operations today.  You now have unfettered access to the spirits on your premises.  Even so, today's rules would seem to exclude totes, for a variety of reasons, that include lack of attached means to gauge and the inability to lock them (visit Section 19.182 to see the full list of what is required). 

I suspect that the ubiquitous totes are a horse that got out of the barn, while TTB slept, and that TTB does not want to cause the hubbub and trouble that attempting to corral them now would cause.  I could, if required, argue a rationale, for purposes of a variance,  that would allow totes, either plastic or stainless, it does not matter,  with a capacity of more than 101 gallons.  But I suspect that they are now allowed, under a don't ask - don't tell policy, with which I chose to silently comply, out of fear of starting something that would cost me nothing and you guys a lot. 

It's been so far so good on the TTB front, but you may have difficulty constructing rationales that provide a way around the state and local safety issues - the picture above of melting totes spilling their contents further to fuel a fire.  I'd be a bit uneasy betting that don't ask don't tell could survive a possible avalanche of enforcement in the wake of such a blaze.   

Again, I think you listen to the experts – this is no place for amateurs like me – and then decide on what risks you want to take.  Perhaps ADI could, as a service to the industry that makes it’s “,com” business possible, contract with a consultant to produce a usable document, written in plain English, that explains it all in ways most can understand. 

Link to comment
Share on other sites

Nabtastic,

I can sell 1000 to 1500 gallon conical vessels for blending and proofing, but for ethanol storage I only have 55 gallon barrels and  stainless totes in sizes up to 750 gallons.  You could certainly stack 2 of the 750s one on top of the other which would make 1500 gallons. I have sold over 70 totes rated for ethonal storage, over the last 6 years.  More than 1/2 of them were used, but I am having a harder time sourcing the used ones since oil prices are going up. I am getting around the rules concerning volume restrictions on storage inside my distillery by storring in UL listed vessels outside the main distillery building in a 3 sided shed that has steel bars and a lock to protect the revenue.  I am not required to have sprinkler systems or anything like that in my distillery.  

 

Link to comment
Share on other sites

Southernhighlande makes an interesting point - nothing precludes you from having outside tanks.  You must include them on your registration (19.72 - Describe each building and outside tank that will be used for production, storage, and processing of spirits ...).  The security requirements (19.192(c) )are simple, "Outdoor tanks containing spirits, denatured spirits, or wine must be individually locked or locked within an enclosure when they are not in use."  I have had barrel storage approved in a roofed structure with two of the four sides made of chain link.  As always, past approval is no guarantee of future approval, but assuming that a shed with two chainlink sides is still approvable, I can't believe that one with four  chain link chain sides would not also be approved.  

Link to comment
Share on other sites

  • 2 weeks later...

Thanks everybody.  I think for our purposes we'll have to store outside.  Paul - if we decide to go with totes, I'll message you. 

Cheers

Link to comment
Share on other sites

  • 8 months later...

good evening all - we have approved construction plans for 3 added zones for transstore tank storage, each at 240 gal maq.   "I think" those zones need to be studwall/sheetrock with individual fire suppression (sprinkler).  However, Is that NFPA or other requirement?  Or can the zones be chain link fence, so we can use the existing F-1 sprinklers?    That would make construction a lot        simpler.   Fire services contractor is recommending chain link, as sprinklers will active at 150 degrees. 

Also for Thatch, is there an updated link?  Keep receiving 404 error on above, and searching at the site does not produce a link.

With thanks,

 

 

Link to comment
Share on other sites

8 hours ago, et1883 said:

Also for Thatch, is there an updated link?  Keep receiving 404 error on above, and searching at the site does not produce a link.

From a recent post I made.  Both links are good.

Don't know about the specific dates but in the current regs fire is exempt but building is not and the toughest test is what you have to meet.  The link provided does a pretty good job of explaining.

 http://www.klausbruckner.com/blog/distillery-storage-dilemmas/

As bluefish says, the barrels count toward your MAQ.  If you are shooting for F-1, you are limited to 120 gallons un-sprinkled and 240 sprinkled.  Beyond that you classified as hazardous.

Another good explanation is from Scott Moore of Dalkita.  It's about an hour long

https://americancraftspirits.org/courses/code-breaking-barrels-revealing-the-mysteries-of-barrel-storage-in-building-and-fire-codes/

  • Thanks 1
Link to comment
Share on other sites

10 hours ago, et1883 said:

good evening all - we have approved construction plans for 3 added zones for transstore tank storage, each at 240 gal maq.   "I think" those zones need to be studwall/sheetrock with individual fire suppression (sprinkler).  However, Is that NFPA or other requirement?  Or can the zones be chain link fence, so we can use the existing F-1 sprinklers?    That would make construction a lot        simpler.   Fire services contractor is recommending chain link, as sprinklers will active at 150 degrees. 

Also for Thatch, is there an updated link?  Keep receiving 404 error on above, and searching at the site does not produce a link.

With thanks,

 

 

Are you trying to build some walls to separate tanks so you can triple your MAQ? If so a chain link fence doesn't slow down fire very well...

  • Thanks 1
Link to comment
Share on other sites

agree with Tom that chain link is not a good fire prevention method.    Thanks to Thatch for links to the 64 page powerpoint and audio above.    Will share these links with our fire services contractor and fire marshall.

Link to comment
Share on other sites

12 hours ago, et1883 said:

good evening all - we have approved construction plans for 3 added zones for transstore tank storage, each at 240 gal maq.   "I think" those zones need to be studwall/sheetrock with individual fire suppression (sprinkler).  However, Is that NFPA or other requirement?  Or can the zones be chain link fence, so we can use the existing F-1 sprinklers?    That would make construction a lot        simpler.   Fire services contractor is recommending chain link, as sprinklers will active at 150 degrees. 

Also for Thatch, is there an updated link?  Keep receiving 404 error on above, and searching at the site does not produce a link.

With thanks,

 

 

Why not just put your storage tanks outside the building?  There are no sprinkler system or fire wall requirements that way.  You don't even need a shed, just locks on the tanks as per the TTB.  If you need a great price on transtore tanks just let us know.

  • Thanks 1
Link to comment
Share on other sites

If you are talking about control areas, then chain link won't do it.  You must have a fire resistant wall that would contain any fire to that room for a specific period of time.

Is your goal to avoid an H-3 classification?

  • Thanks 1
Link to comment
Share on other sites

hoping to avoid H3 but starting to see no way around it.  Southernhighlander's outside storage idea has been posed to landlord.   From some of the charts it seems that ventilation, power back up, alarms are the primary differences between F-1 and H3 (other than volume, of course). 

Link to comment
Share on other sites

1 hour ago, Southernhighlander said:

Why not just put your storage tanks outside the building?  There are no sprinkler system or fire wall requirements that way.  You don't even need a shed, just locks on the tanks as per the TTB.  If you need a great price on transtore tanks just let us know.

About building and fire codes I know nothing, but for those who want to know the source of Southhighlander' s  contention,  §19.192 discusses where you must use TTB approved locks:

  • Subsection (e) Approved locks. Locks meeting the specifications prescribed in paragraph (f) of this section must be used to secure:  (1) Outdoor tanks used to store spirits, OR an enclosure around such tanks." The emphasis is mine, but "or" is disjunctive.  It is one or the other and  I'd advise both as a way of securing your assets, even if TTB settles for just one. 

TTB hasn't been very strict about enforcing tank requirements for inside tanks. Compare what you see to what it requires below to verify that comment.  I suspect that it would be more stringent with outside tanks, so visit  §19.182, which requires, in pertinent part,  that all tanks be:

  • Equipped with accurate means for measuring their contents. If the means for measurement is not a permanent fixture on the tank, the proprietor must equip the tank with a fixed device for measuring the contents. However, tanks having a capacity of less than 101 gallons are not required to have permanent gauge devices;
  • Accurately calibrated if used for any of the gauges described in this part [for example, an inventory :-)].  Further, if tanks or their gauging devices are moved in any manner subsequent to original calibration, the tanks shall not be used until recalibrated;
  • Accessible through walkways, landings, and stairs that permit access to all parts of the tank [TTB must be able to reach the top safely];
  • Equipped or situated so that they may be locked or secured [this includes  manholes as well as valves]; and
  • Constructed to prevent access to the spirits or wines through vents, flame arresters or other safety devices.  

Generally, there are no taxes due on spirits that are lost, but hen it appears that a theft occurred, the burden of proof will be on the proprietor or other person liable for the tax to establish to the satisfaction of the appropriate TTB officer that the theft did not result from connivance, collusion, fraud, or negligence on the part of the proprietor, owner, consignor, consignee, bailee, or carrier, or any employee or agent of any of them."  That one cannot prove a negative is obvious, so how do you prove that no employee was involved?  In practice, some  of the burden will fall on TTB to prove that an employee was involved.  But TTB is likely to determine that theft from a tank  that is not constructed as required by §19.182 is the result of your negligence.  Even if TTB accepts an offer-in-compromise of dimes on the dollar, as it has done in at least one case, because  tanks hold a lot of spirits, the amount you end up paying can be significant.  So, if you use an outside tank, make sure the tank complies with the rules.
 

  • Thanks 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...